Two alternators are running in parallel to supply the following loads: LOAD 1, 400KW at unity power factor LOAD 2, 500KW at 0.9 lagging power factor LOAD 3, 600KW at 0.866 lagging power factor. If...


Two alternators are running in parallel to supply the following loads:


LOAD 1, 400KW at unity power factor


LOAD 2, 500KW at 0.9 lagging power factor


LOAD 3, 600KW at 0.866 lagging power factor.


If alternator A is loaded to 1,000KW at 0.94 lagging power factor, what will be the load of Alternator B and its corresponding power factor?