The single-line diagram of a power system in shown in the figure. The reactance data for the power system shown in the figure in per unit on a common base are as follows; T1 T2 3 2 4 G1 G2 Item X1 X2...


The single-line diagram of a power system in shown in the figure. The reactance data for the power system shown in the figure<br>in per unit on a common base are as follows;<br>T1<br>T2<br>3<br>2<br>4<br>G1<br>G2<br>Item<br>X1 X2 X0<br>G1<br>0.100.100.05<br>G2<br>0.100.100.05<br>T1<br>0.25 0.25 0.25<br>T2<br>0.25 0.25 0.25<br>Line 1-20.300.300.50<br>1. Draw the positive, negative and zero sequence networks and obtain the Thevenin equivalent circuits<br>2. Find the fault current for a single line to neutral (SLG) fault as shown in Bus 1.<br>

Extracted text: The single-line diagram of a power system in shown in the figure. The reactance data for the power system shown in the figure in per unit on a common base are as follows; T1 T2 3 2 4 G1 G2 Item X1 X2 X0 G1 0.100.100.05 G2 0.100.100.05 T1 0.25 0.25 0.25 T2 0.25 0.25 0.25 Line 1-20.300.300.50 1. Draw the positive, negative and zero sequence networks and obtain the Thevenin equivalent circuits 2. Find the fault current for a single line to neutral (SLG) fault as shown in Bus 1.