Analyze the WLHP system in worked example 13.13 including a water storage tank of volume 2m3 , if each time period is 6 hours.   Example 13.13 An office building has the following occupancy schedule...


Analyze the WLHP system in worked example 13.13 including a water storage tank of volume 2m3 , if each time period is 6 hours.




Example 13.13


An office building has the following occupancy schedule during a typical week. (i) From Monday to Friday it is fully occupied from 7 a.m. to 7 p.m. (12 hours) and unoccupied during the rest of the day. (ii) It is unoccupied on Saturday and Sunday. The UA-value for the building is 1.75 kW°Cí1 . The internal heat gains and the indoor  temperatures during the occupied and unoccupied periods are respectively, 14.8 kW, 22°C and 1.3 kW, 18°C. The building is heated by a fuel-fired furnace of capacity of 80 kW and efficiency 88%. Assume a degradation coefficient of 0.25 due to cycling of the furnace. The annual bin data for the three consecutive 8-hour periods, obtained from Ref. [3] are given in Table 13.13.1. Estimate the annual heating loads and heating energy inputs to the furnace for the occupied and unoccupied periods.






May 26, 2022
SOLUTION.PDF

Get Answer To This Question

Related Questions & Answers

More Questions »

Submit New Assignment

Copy and Paste Your Assignment Here