An air conditioning system, shown schematically in Fig. 5.10(a), supplies air at the rate of 4 kgsí1 to a space maintained at a dbtemperature of 27°C and relative humidity of 50%. The sensible and...


An air conditioning system, shown schematically in Fig. 5.10(a), supplies air at the rate of 4 kgsí1 to a space maintained at a dbtemperature of 27°C and relative humidity of 50%. The sensible and latent heat loads on the space are 46 kW and 20 kW respectively. Outdoor air at 35°C db-temperature and 24°C wb-temperature is introduced at the rate of 1.1 kgsí1 . The relative humidity of the air leaving the cooling coil is 90%. The pressure is constant at 101.3 kPa. Determine (i) the supply air temperature and relative humidity, (ii) the mass flow rate of the air that bypasses the cooling coil, and (iii) the refrigeration capacity of the cooling coil.



May 26, 2022
SOLUTION.PDF

Get Answer To This Question

Related Questions & Answers

More Questions »

Submit New Assignment

Copy and Paste Your Assignment Here