A three-phase fault with a fault impedance Zf = jo.16 per unit occurs at bus 3 in the Figure beside, Using the bus impedance matrix method, the bus impedance matrix for this system is: j0.16 j0.08...


A three-phase fault with a fault impedance Zf =<br>jo.16 per unit occurs at bus 3 in the Figure<br>beside, Using the bus impedance matrix<br>method,<br>the bus impedance matrix for this system is:<br>j0.16 j0.08 j0.12<br>Zu =| j0.08 j0.24 j0.16<br>30.12 j0.16 j0.34<br>ーブ5<br>ー2.5<br>ー1.25<br>ープ2.5<br>-j2.5<br>Ve = V3(0)<br>Is(F)<br>[X<br>|| Z, = j0.16<br>The bus voltage of Bus1 (V,(F) in p.u is:<br>Answer:<br>0.76 p.u<br>

Extracted text: A three-phase fault with a fault impedance Zf = jo.16 per unit occurs at bus 3 in the Figure beside, Using the bus impedance matrix method, the bus impedance matrix for this system is: j0.16 j0.08 j0.12 Zu =| j0.08 j0.24 j0.16 30.12 j0.16 j0.34 ーブ5 ー2.5 ー1.25 ープ2.5 -j2.5 Ve = V3(0) Is(F) [X || Z, = j0.16 The bus voltage of Bus1 (V,(F) in p.u is: Answer: 0.76 p.u