A 500-MVA 20-kV, 60-Hz synchronous generator with reactances X, = 0.15, X= 0.24; X=1.1 per unit and time constants T = 0.035, T, = 2.0, T= 0.20 s is connected to a circuit breaker. The generator is...


A 500-MVA 20-kV, 60-Hz synchronous generator<br>with reactances X, = 0.15, X= 0.24; X=1.1<br>per unit and time constants T = 0.035, T, = 2.0,<br>T= 0.20 s is connected to a circuit breaker. The<br>generator is operating at 5% above rated<br>%3D<br>voltage and at no-load when a bolted three-<br>phase short circuit occurs on the load side of<br>the breaker. The breaker interrupts the fault 3<br>cycles after fault inception. On abase of<br>500MVA, 20KV.<br>The subtransient fault current in kA rms is:<br>Answer: I

Extracted text: A 500-MVA 20-kV, 60-Hz synchronous generator with reactances X, = 0.15, X= 0.24; X=1.1 per unit and time constants T = 0.035, T, = 2.0, T= 0.20 s is connected to a circuit breaker. The generator is operating at 5% above rated %3D voltage and at no-load when a bolted three- phase short circuit occurs on the load side of the breaker. The breaker interrupts the fault 3 cycles after fault inception. On abase of 500MVA, 20KV. The subtransient fault current in kA rms is: Answer: I"= 101.0 kA