A 100kW, 230V, shunt generator has an armature resistance and field resistance of 0.050 and 57.50. If the generator operates at rated voltage (a) Calculate the induced voltage at half-load, neglect...


A 100kW, 230V, shunt generator has an armature resistance and field resistance of<br>0.050 and 57.50. If the generator operates at rated voltage<br>(a) Calculate the induced voltage at half-load, neglect the brush contact drop.<br>If SPL is 1.8kW, calculate<br>(b) Generator efficiency at full-load.<br>(c) Horsepower output from the prime mover to drive the generator at full load.<br>

Extracted text: A 100kW, 230V, shunt generator has an armature resistance and field resistance of 0.050 and 57.50. If the generator operates at rated voltage (a) Calculate the induced voltage at half-load, neglect the brush contact drop. If SPL is 1.8kW, calculate (b) Generator efficiency at full-load. (c) Horsepower output from the prime mover to drive the generator at full load.