5. The zero-, positive-, and negative-sequence bus impedance matrices for a three-bus power system are given below [0.10 0.15 0.12] Zus =j 0.15 0.10 0.08 %3D pu L0.12 0.08 0.35] [0.16 0.10 0.15] ZBus...


5. The zero-, positive-, and negative-sequence bus impedance matrices for a three-bus<br>power system are given below<br>[0.10 0.15 0.12]<br>Zus =j 0.15 0.10 0.08<br>%3D<br>pu<br>L0.12 0.08 0.35]<br>[0.16 0.10 0.15]<br>ZBus = ZBus =j0.10 0.20 0.14 pu<br>Lo.15 0.14 0.30]<br>%3D<br>Determine the per unit fault current and the bus voltages during fault for<br>(a) A bolted three-phase fault at bus 2.<br>(b) A bolted single line-to-ground fault at bus 2.<br>(c) A bolted line-to-line fault at bus 2.<br>(d) A bolted double line-to-ground fault at bus 2.<br>

Extracted text: 5. The zero-, positive-, and negative-sequence bus impedance matrices for a three-bus power system are given below [0.10 0.15 0.12] Zus =j 0.15 0.10 0.08 %3D pu L0.12 0.08 0.35] [0.16 0.10 0.15] ZBus = ZBus =j0.10 0.20 0.14 pu Lo.15 0.14 0.30] %3D Determine the per unit fault current and the bus voltages during fault for (a) A bolted three-phase fault at bus 2. (b) A bolted single line-to-ground fault at bus 2. (c) A bolted line-to-line fault at bus 2. (d) A bolted double line-to-ground fault at bus 2.