1. A 100kW, 230V, shunt generator has an armature resistance and field resistance of 0.050 and 57.50. If the generator operates at rated voltage (a) Calculate the induced voltage at half-load, neglect...


please answer the following


1. A 100kW, 230V, shunt generator has an armature resistance and field resistance of<br>0.050 and 57.50. If the generator operates at rated voltage<br>(a) Calculate the induced voltage at half-load, neglect the brush contact drop.<br>If SPL is 1.8kW, calculate<br>(b) Generator efficiency at full-load.<br>(c) Horsepower output from the prime mover to drive the generator at full load.<br>DC Shunt Generator<br>

Extracted text: 1. A 100kW, 230V, shunt generator has an armature resistance and field resistance of 0.050 and 57.50. If the generator operates at rated voltage (a) Calculate the induced voltage at half-load, neglect the brush contact drop. If SPL is 1.8kW, calculate (b) Generator efficiency at full-load. (c) Horsepower output from the prime mover to drive the generator at full load. DC Shunt Generator

Jun 11, 2022
SOLUTION.PDF

Get Answer To This Question

Related Questions & Answers

More Questions »

Submit New Assignment

Copy and Paste Your Assignment Here